Issue
Only one of the readers on a 7920 DPU works
Environment
7920 DPU
Cause
If you have defined one door in the DPU 7920, and the door’s Exit Reader parameter is set to anything other than "NO," then the second reader port automatically becomes the exit reader.
Resolution
If you have defined two doors in a DPU 7920, neither door can have an Exit Reader defined.