Only getting the RTN of an alarm (or vice versa)
  • Only getting the RTN of an alarm (or vice versa)
  • AbeMeran
    AbeMeran
‎2018-09-11 12:59 AM
When point goes in alarm nothing is displayed in the active alarm viewer but when the point returns to normal the RTN shows up in the alarm viewer.
CyberStation
The Alarm Enrollment allows you to specify the transitions that gets sent to the active alarm viewer, make you the appropriate check boxes are checked.
Configure the alarm enrollment to deliver both the alarm and the RTN