One of the properties for the LON object in the 511 is 'Use subnet node addressing' what does this do?
  • One of the properties for the LON object in the 511 is 'Use subnet node addressing' what does this do?
  • sesa150555
    sesa150555
‎2018-09-06 03:06 PM
  • Xenta 511 LTA
  • LON Network
If you import a LNS network into XBuilder and are going to use polled values from a LonWorks devices, you can choose if the Xenta 511 is going to use subnet/node or neuron ID to address the current LonWorks devices.
The advantage to using subnet/node addressing is that importing the LNS network into XBuilder again if node is replaced in the LNS network is not necessary, provided that the node keeps the same subnet/node and the same application.