Offline Xenta 401 Not Generating Alarms
  • Offline Xenta 401 Not Generating Alarms
  • Derrick_Ratliff
    Derrick_Ratliff
‎2018-09-06 01:29 PM
Xenta 401
Xenta Group
Xenta Group Master is offline
Determine if the Group Master is offline
  1. In the Vista System Plug-in TAC Network Pane, the Xenta Group Master will be the only controller in the Xenta Group that is underlined
  2. Determine if this controller is offline in LonMaker or NL220
  3. If the group Master or any of the Xenta devices in that Xenta Group show an " * ", you will need to download application and parameters
Change the Group Master to a more reliable controller
  1. Determine which controller in the Xenta group has the least amount of potential traffic
  2. In the Vista System Plug-in TAC Network Pane, Right-Click on this device and select "Set as Master".
  3. Download Application and Parameters to any device that shows and " * " after this change.
  • 5813