Object Transfers are not working after upgrading Vista.
  • Object Transfers are not working after upgrading Vista.
  • sesa177673
    sesa177673
‎2018-09-11 03:58 AM
Object Transfers are not working after upgrading Vista. The devices are online and the values are updated when viewed, but the values aren't transferred via the object transfer objects.
Vista 5.1.X that has been upgraded.
The vista server is in engineering mode.
Go to the $System object under the TAC Vista root object in workstation and check the  Status-Operating check-box is checked.
Tags (2)
  • 13432
  • PeterLarsen24