OPC UA export clarification

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • OPC UA export clarification
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Jonas_Brissman
    Jonas_Brissman

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
341 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

OPC UA export clarification

Janeway Jonas_Brissman Janeway
‎2025-08-26 02:55 AM

on ‎2025-08-26 02:55 AM

Issue

After adding an OPC UA server to EBO an export is done from the Device discovery tab to find the objects in the OPC UA server.
When the OPC UA server database is big this can take up to a day to finish and sometimes the export is never finished.

Product Line

EcoStruxure Building Operation

Environment

Building Operation Workstation

Cause

In EBO version 7 there is a workaround for this issue, it is possible to split the export up in smaller pieces and export objects from specified folders from the OPC UA server instead of all objects in the OPC UA server database.  

Resolution

Introduction

The ‘Export configuration’ section in the settings dialog for discovered devices makes it possible to configure the export procedure. By setting the parameters in this section, you can specify the start node and the depth for each export file. This means that you can break down the export into many files instead of one large file containing everything. When importing the series of export files it is recommended to keep the same structure as the OPC UA server has, but it is not a requirement. You can import the export file anywhere under the device, but again, the recommendation is to keep the same structure as on the OPC UA server.

 

Selecting start node for browse

The start node is specified by setting the ‘Start node namespace index’ (specified as an integer value) and the ‘Start node identifier’ (specified as a string value). The supported ‘Start node identifier’ types are string (s=), integer (i=), opaque (o=) and guid (g=). Both ‘Start node namespace index’ and ‘Start node identifier’ are found as properties on each OPC UA object. If these values are empty, faulty, equal to the object node or equal to the root node, the device object is included in the export file. Otherwise, it is omitted.

Selecting the depth of browse

The depth of an export file is specified as an integer value. It is recommended that this is set to a low number if the export time is expected to take a long time. Values 0, -1 or empty means that no depth limit is used.

Getting started

 

A first step could be to export the root objects. The following configuration will handle that:

Jonas_Brissman_1-1756105722198.png

The export file with this configuration will produce the following result when imported. Since the ‘Start node namespace index’ and the ‘Start node identifier’ are empty, the device object is included, and the import can be done on the ‘OPC UA Client Network’ object

Jonas_Brissman_0-1756111816228.png
Only the root objects were included in the export file since the ‘Export depth’ was set to ‘1’. Next, we would like to populate the ‘BuildingAutomation’ object with 2 levels of child objects. For that we need the namespace index and the identifier of the ‘BuildingAutomation’ object found at the bottom of the property list:

 

Jonas_Brissman_1-1756111858582.png

These values are entered into the export configuration:

Jonas_Brissman_3-1756105775132.png

The export file with this configuration will produce the following result when imported on the ‘BuildingAutomation’ object:

Jonas_Brissman_4-1756105836237.png

Now we have a structure with all the root objects. All of them are empty except for BuildingAutomation that has two levels of child objects.

 

If you realize that the depth chosen was to low, you can simply set the ‘Export depth’ to a higher value and create a new export file from the same start node. The ‘Export configuration’ will now look like below:

Jonas_Brissman_5-1756105867854.png

When importing the new export file we still use the ‘BuildingAutomation’ object as the start object, but since we already have two level of child nodes we need to select the merge option in the import dialog as in the picture below:

Jonas_Brissman_6-1756105889049.png

 


 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • JonasBrissman25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore