Not recommended to use XBuilder time schedules to control I/NET controllers
  • Not recommended to use XBuilder time schedules to control I/NET controllers
  • SESA116857
    SESA116857
‎2018-09-06 03:07 PM
Using Time Schedules in the Xenta 527
  • Xenta 527
  • I/NET system
  • I2V integration
Users should exercise caution when creating time schedule objects and pages in the Xenta 527. If a time schedule is created and directed at an I/NET point that already has a time schedule on the controller, the point value will be incorrect until the schedules synchronize.
Due to the risk of improper results, possible harm to equipment in an HVAC environment, possible security breaches in a security environment, and the risk that if Ethernet communications fail the point will not operate according to the schedule it is recommended that time schedules in the 527 not be used with I/NET points.
The I/NET time schedule object, which is created during the save file conversion in XBuilder, should be used . This object will direct you to a page that modifies the I/NET time schedule on the controller.
Labels (2)
  • TAC INET
  • 1960