Not able to discover the MNB controllers on the MSTP trunk of an AS.
  • Not able to discover the MNB controllers on the MSTP trunk of an AS.
  • sesa116873_brid
    sesa116873_brid
‎2018-09-06 09:27 AM
Not able to discover the MNB controllers on the MSTP trunk of an AS. However, all MNB controllers on the same AS trunk are discovered in WorkPlace Tech Commissioning Tool.
SmartStruxure, AS
The negative lead of the MS/TP AS network was shorted to ground.
Examine all MS/TP wiring and correct any grounding issue.
  • 16625