No alarm be triggered when the door is opening for a long time.
  • No alarm be triggered when the door is opening for a long time.
  • YangboLIU
    YangboLIU
‎2018-09-06 10:06 AM
When configure a door with both reader channels as 0, only want to monitor the status of door switch, when the door is opening for a long time, the door ajar alarm should be triggered if the alarm has been configured, but on this condition, the door ajar alarm will never be triggered.
Cyberstation
ACX
AC-1
Maybe it is a design, the controller not consider is a door when the reader channel is 0
Set a valid channel number for EntryReader although it is not connected, then try again, that should be OK.
  • 14288