Niagara workaround for routers that do NOT support Extended Frames

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Niagara workaround for routers that do NOT support Extended Frames
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Purser
    David_Purser

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
509 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Niagara workaround for routers that do NOT support Extended Frames

Picard David_Purser Picard
‎2025-08-04 01:15 PM

Issue

Routers or devices with routing capabilities may not support BACnet Protocol 16 Extended Frames (1474 bytes) and only support BACnet MSTP Frame size (480 bytes), so devices that support the larger size need to receive a request with a smaller APDU defined or they will use the largest APDU they support, which will be dropped at the router. Each BACnet device has a Max APDU Length Accepted property and SpaceLogic/Easylogic, which supports Extended Frames, is 1474 bytes.

Product Line

TAC IA Series

Environment

  • MP-X under Tridium offer
  • SE branded Tridium offer
  • I/A Series MNB 1000
  • Building Operation EasyLogic RP-C
  • Building Operation EasyLogic RP-V
  • Building Operation EasyLogic MP-C
  • Building Operation EasyLogic RP IO Expansion Module
  • Building Operation Multi-purpose Controller
  • Building Operation Multi-purpose VAV

Cause

Routers and devices, acting as routers, that support BACnet Protocol Revision lower than 16 will drop the extended frames (aka large packets). BACnet Protocol 16 introduced Extended Frames (1474 bytes) to BACnet MSTP, which increased the frame size from 480 bytes. BACnet devices have Max APDU Length Accepted, which communicates the largest frame size accepted. SpaceLogic/Easylogic have Max APDU Length Accepted =  1474 bytes.

Resolution

  1. Add bacnetUtil-rt module to the station, which is included in default Niagara installation, using Platform -> Software Manager.
  2. Open Palette -> bacnetUtil
  3. Select ApduSizeOverride from DeviceOverrides folder
  4. Drag-n-drop it on the BACnet controller
  5. The default is 480 for BACnet MSTP. To disable for SpaceLogic/EasyLogic controllers communicating via IP or on MSTP supporting Extended Frames, you can change to 1474 to match the CONFIG -> Device Object -> Max APDU Length Accepted. ApduSizeOverride.png

NOTE A: This can be added to any device, so changing to 480 will indicate how much slower communication would be if using an MSTP router that does not support Extended Frames. I tried by viewing Device Report in N4.14 while capturing in Wireshark, so I could see packet timing on the wire, and it was about 3 times slower.

ApduSizeOverride # of Request Required Period
480 46 17.13 secs
1474 14 6.76 secs
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • DavidPurser25
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore