Issue
A new Niagara R2 UNC is installed with a license. The license installs correctly. After a reboot, the station fails to start. The standard output window displayed a fatal error as illustrated below:
Product Line
TAC IA Series
Environment
Niagara R2
Cause
Certain foreign characters are not recognized by Tridium's License Generator. In this case, a French character (with a symbol above the letter) was used in the customerSite name. When the license was generated, the French character converted to a question mark (?):
customerSite=Rotondle des S?urs
The ? symbol is not recognized by Niagara. So, when an UNC is rebooted, it will read the license file and stop when it comes to the customerSite name.
Resolution
Contact the factory to have the license modified.
After correction by the factory, the customerSite line in the license example above reads:
customerSite=Rotondle des Seurs