Niagara R2 Error: "Cannot open web server socket. [ServerLoop.run] java.net.BindException: Address already in use: JVM_Bind"

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Niagara R2 Error: "Cannot open web server socket. [ServerLoop.run] java.net.BindException: Address already in use: JVM_Bind"
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa116873_brid
    sesa116873_brid
  • Leo_Tantalo
    Leo_Tantalo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3134 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Niagara R2 Error: "Cannot open web server socket. [ServerLoop.run] java.net.BindException: Address already in use: JVM_Bind"

Picard Product_Support
‎2018-09-06 12:38 PM

Issue

Getting the following error message when attempting to open a Niagara R2 Enterprise Server station:

ERROR: Cannot open web server socket. [ServerLoop.run]
java.net.BindException: Address already in use: JVM_Bind
at java.net.PlainSocketImpl.socketBind(Native Method)
at java.net.PlainSocketImpl.bind(Unknown Source)
at java.net.ServerSocket.bind(Unknown Source)
at java.net.ServerSocket.(Unknown Source)
at tridium.nre.drivers.SocketDriver$TcpSocketFactory.createServerSocket(SocketDriver.java:681)
at tridium.nre.drivers.SocketDriver.createServer(SocketDriver.java:203)
at tridium.foundation.net.TWebServer$ServerLoop.run(TWebServer.java:754)
at java.lang.Thread.run(Unknown Source)

Product Line

TAC IA Series

Environment

Niagara R2 Enterprise Server all version

Cause

Windows IIS is enabled on Enterprise Server PC. IIS and WorkPlace Pro (station database) have a conflict issue related to Port 80. By default, IIS connects and utilizes Port 80 when installed and running. This directly conflicts with an Enterprise Server’s station database running on the PC which also uses Port 80 by default.

Resolution

Most times, users do not require IIS on the Enterprise Server or WorkPlace Pro PC so IIS is disabled. If IIS is required, users typically change the port used by the station's database to another port (e.g. 8080, etc.). If this change is made, all other settings that access this IP for the station (address table entries, web browser pages, etc.) must append the port number to the IP address (e.g. 192.168.1.142:8080).

Disable the IIS if not required by some other application on the Enterprise Server PC.

  1. Select Start and open the Control Panel
  2. Double-click add remove program
  3. Click on “Add/Remove Windows Components on left side on screen
  4. Scroll down and deselect Internet Information Services in the Components window
  5. Click next and Finish

The Enterprise Server station can now be opened.

Note:  On Windows 7 host computer, the World Wide Publishing Service may be linked to IIS.  Go to 'Services' in Windows 7 and modify its startup to 'Manual' so that it does not start automatically. 

If IIS is needed on the Enterprise Server PC, then change the port used by the Enterprise Server.

  1. Open WorkPlace Pro Admin Tool and stop the Enterprise Server
  2. Open the Enterprise Server offline
  3. Right-click on the Enterprise Server station and open its Properties sheet
  4. Click on the Config tab
  5. Change httpPort to the desired port number and click Apply
  6. Right-click on the Enterprise Server and Save
  7. Close the Enterprise Server station
  8. Open Admin Tool and start the Enterprise Server station 

Once the station starts you should now be able to access it. Please note that the port number must now be included in the station's address when accessing the Enterprise Server.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 7392
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of