Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Niagara NTP Troubleshooting

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Niagara NTP Troubleshooting
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
4643 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Niagara NTP Troubleshooting

RandyDavis Champion
‎2024-10-15 09:32 AM

Issue

Configuring NTP and troubleshooting in the Niagara Frameworks

Product Line

TAC IA Series

Environment

  • I/A Series N4 Enterprise Server
  • I/A Series N4 Jace

Cause

Guide to configure and test NTP server and Jace sync operations

Resolution

Please familiarize yourself with the official documentation of the NTP functionality. NTP and its configuration are comprehensively documented in the Niagara Platform Document. The official documentation is updated frequently and may contain information that supersedes the content of this article.

Using the ntpq utility program

The NTP Project maintains the NTP software that is compiled and included with Red Hat Enterprise Linux (and other most other Linux distributions). To get the software for Microsoft Windows, Meinberg ports the software and provides it. With this software, you not only get the ntpq utility program, you also can run the NTP client/server on your PC. In this way, you can use your PC as an NTP time server to your JACE.

  • NOTE: The Client and Server (Time Only) options were added in 4.9. Using Server creates potential attack surface for 'Mode 6' queries. But to query with ntpq as described below, it must be set to Server, at least temporarily. Be advised that you should not have your JACE exposed to the Internet. Consult the Niagara Cyber Defense page for more details.

Using the ntpq utility program, you can query a JACE that is configured for NTP, and get a list of the peers known to the JACE and a summary of their state. For this use the -p option, and provide the IP address to the JACE. The command will look like this:

  • ntpq -p 192.168.1.140
    The output of the command will look something like this:

    NTP_1.png

    The ntpq man page at ntp.org fully documents the details of the table above. Only a few details will be covered here. 

  • The row that begins with * (asterisk), has been declared the system peer.

  • The second row begins with a space, indicating that it is an unreachable peer. 

  • The third column is for the stratum. Stratum 0 is an actual time source, like an atomic clock, that provides time to a stratum 1 NTP server. A stratum 2 server gets its time from a stratum 1 server. A stratum 3 server gets its time from a stratum 2 server, and so on. 

  • Reach is a circular log buffer containing a set of eight bit-flags, expressed as an octal number. Convert octal to binary to determine the reach for the last eight attempts. For example, 376 converts to 11111110, which means that we failed to reach the server the last time, but the other 7 were successful. 

 

Using the NtpPlatformServiceQnx spy page

  1. Right-click the NtpPlatformServiceQnx and select Views > SpyRemote.
         NTP_2.png

     

  2. As you scroll down the first section of interest is the one that shows the NTP Configuration File. It reads what we've written to the file ntp.conf and displays it.

                                             NTP Configuration File
    #/home/niagara/etc/ntp.conf: Niagara Network Time Protocol Configuration File
    #Use the NtpPlatformService UI to modify this file.
    #Created: 24-Sep-19 4:53 PM EDT
    #
    #Niagara NtpPlatformService variable, do not modify
    #ntpEnabled true
    #syncAtBoot true

    #server list
    server 192.168.1.2 burst prefer
    server 192.168.1.3 burst
    server 192.168.1.4 burst
    peer 192.168.1.5
    peer 192.168.1.6
    #ntp features enabled
    enable ntp stats

    #ntp panic value, if offset exceeds this, ntpd should exit (disabled if 0)
    tinker panic 0

    #gather information about statistics
    statistics clockstats loopstats
    filegen clockstats file clockstats type none nolink enable
    filegen loopstats file loopstats type none nolink enable
  3. The next section of interest is for the NTP Daemon Log. You'll only see this section if Generate NTP Statistics is set to true. It's generally not necessary to consider these statistics. 

                                                         Generate NTP Statistics
    Jan 30 08:45:14 nto ntpd[8740900-1]: receive: Unexpected origin timestamp 0xe1dd1553.126c40f0 does not match aorg 0000000000.00000000 from sym_active@172.16.10.197 xmt 0xe1dd161a.aa0c9b85
    Jan 30 08:46:14 nto ntpd[8740900-1]: receive: Unexpected origin timestamp 0xe1dd1552.126c471e does not match aorg 0000000000.00000000 from sym_active@172.16.10.99 xmt 0xe1dd1656.2b9be356
    Jan 30 08:46:18 nto ntpd[8740900-1]: receive: Unexpected origin timestamp 0xe1dd1553.126c40f0 does not match aorg 0000000000.00000000 from sym_active@172.16.10.197 xmt 0xe1dd165a.aa0c9453
    Jan 30 08:47:18 nto ntpd[8740900-1]: receive: Unexpected origin timestamp 0xe1dd1552.126c471e does not match aorg 0000000000.00000000 from sym_active@172.16.10.99 xmt 0xe1dd1696.2b9bca8b
    Jan 30 08:47:22 nto ntpd[8740900-1]: receive: Unexpected origin timestamp 0xe1dd1553.126c40f0 does not match aorg 0000000000.00000000 from sym_active@172.16.10.197 xmt 0xe1dd169a.aa4e33f0
    Jan 30 08:48:22 nto ntpd[8740900-1]: receive: Unexpected origin timestamp 0xe1dd1552.126c471e does not match aorg 0000000000.00000000 from sym_active@172.16.10.99 xmt 0xe1dd16d6.2b9bd269
    Jan 30 08:48:29 nto ntpd[8740900-1]: receive: Unexpected origin timestamp 0xe1dd1553.126c40f0 does not match aorg 0000000000.00000000 from sym_active@172.16.10.197 xmt 0xe1dd16dd.aa8fa9b9
    Jan 30 08:49:27 nto ntpd[8740900-1]: receive: Unexpected origin timestamp 0xe1dd1552.126c471e does not match aorg 0000000000.00000000 from sym_active@172.16.10.99 xmt 0xe1dd1717.2b9bcbe9
    Jan 30 08:49:34 nto ntpd[8740900-1]: receive: Unexpected origin timestamp 0xe1dd1553.126c40f0 does not match aorg 0000000000.00000000 from sym_active@172.16.10.197 xmt 0xe1dd171e.aad12b7e
    Jan 30 08:51:18 nto ntpd[8740900-1]: receive: Unexpected origin timestamp 0xe1dd1203.21caf133 does not match aorg 0xe1dd175e.153d05cf from sym_active@172.16.11.205 xmt 0xe1dd1786.c4cb59c2
    Jan 30 08:51:33 nto ntpd[8740900-1]: receive: Unexpected origin timestamp 0xe1dd11bb.218961dc does not match aorg 0xe1dd175c.153d0991 from sym_active@172.16.10.171 xmt 0xe1dd1795.1de9a94c
    Jan 30 08:51:40 nto ntpd[8740900-1]: receive: KoD packet from 172.16.10.158 has a zero org or rec timestamp. Ignoring.
    Jan 30 08:52:44 nto ntpd[8740900-1]: receive: KoD packet from 172.16.10.158 has a zero org or rec timestamp. Ignoring.
  4. The next section is NTP Daemon Drift. After NTP has synchronized with reliable time servers for a significant amount of time, it will write the calculated drift (in PPM) to a file, such that it can initialize with this value on reboot. It will use this calculation of how far the clock drifts, to correct the clock in real-time, in increments too small for any application to detect.  
    NTP Daemon Drift
    20.185  
  5. NTP Daemon Clock Stats is next. It reads what is in the clockstats file. In this example output, the file does not exist and the spy page tells us so. 
                                                       NTP Daemon Clock Stats
    Modified Julian Day | Secs. Past UTC Midnight | Clock Address | Last Time Code
    Error reading /var/run/ntpdstats/clockstats: /var/run/ntpdstats/clockstats (No such file or directory)
  6. The final section of interest is NTP Daemon Loop Stats. If you're not getting data here, then the configured servers/peers might not be reachable. 
     
    NTP Daemon Loop Stats
    Modified Julian Day | Secs. Past UTC Midnight | Time Offset Secs. | Drift Compensation | Estimated Error | Stability | Polling Interval
    58860 29871.775 0.000000000 20.226 0.000976563 0.000000 6
    58860 30081.780 0.000753215 20.226 0.000976563 0.000000 6
    58860 30150.781 0.000753034 20.226 0.000976563 0.000000 6
    58860 30688.793 0.000018819 20.227 0.000976563 0.000213 6
    58860 31155.803 -0.000220479 20.220 0.000976563 0.002179 6
    58860 31221.804 0.002128888 20.229 0.001234668 0.003595 6
    58860 31233.872 -0.001539013 20.228 0.001736532 0.003385 6
    58860 31385.925 -0.000336908 20.225 0.001679057 0.003345 6
    58860 31498.941 0.000431773 20.228 0.001608116 0.003294 7
    58860 31841.815 0.000467697 20.230 0.001543370 0.003195 7
    58860 32276.675 0.000795988 20.235 0.001484403 0.003499 7
    58860 32546.942 0.009518751 20.274 0.003382136 0.013979 7
    58860 32666.611 0.000412569 20.274 0.004513791 0.013078 7

     
Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (1)
  • Find more articles tagged with:
  • RandyDavis24
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore