Niagara G3 locks up Internet Explorer browser with a gray or white screen
  • Niagara G3 locks up Internet Explorer browser with a gray or white screen
  • Kim_Baze
    Kim_Baze
‎2018-09-06 02:32 PM
In a Niagara G3, when going from graphic to graphic via the IE browser a gray or white screen will be displayed and the browser will lock up. The number of screens viewable before this happens is random.
  • Niagara G3
  • Internet Explorer
The G3 Niagara software was designed to function using the standard JRE. Therefore, it will be necessary to disable a setting in the Java control panel if this symptom is experienced.
  1. Go to Control Panel and click on Java to open the Java Control Panel.
  2. Click on the Advanced tab and then expand the Java Plug-in setting.
  3. Uncheck the box for "Enable next generation Java Plug-in (requires browser restart)" and click on Apply.
    Note: In rare cases with very large graphics files the Java Console could show the following error: "java.lang.OutOfMemoryError: Java heap space". If this is experienced it is possible to adjust the Heap space.
    1. Go to the Control Panel and click on Java to open the Java Control Panel.
    2. Click on the Java tab and click on the "view..." button to display the Java Runtime Environment Settings.
    3. For the Java version enabled you will need to add parameters to the "Runtime parameters". In the single case where this was necessary the Runtime parameters used were "-Xms128m -Xmx256m".
    4. After adjusting the Java Heap, clear out the wbapplet cache.
      1. Go to Windows Explorer - Local Disk C: - Documents and Settings - Your Admin folder
      2. Right click on the "niagara" folder and delete it.
      3. This folder and its subfolders and files will be recreated the next time you open the browser.
  • TAC IA Series
  • 3669