Niagara G3 kitControl Minimum, Maximum, and Average outputs go to Nan if any inputs are Nan
  • Niagara G3 kitControl Minimum, Maximum, and Average outputs go to Nan if any inputs are Nan
  • SESA113595
    SESA113595
‎2018-09-10 03:49 AM
Last Updated: Administrator DavidFisher Administrator ‎2019-08-23 08:03 AM
The outputs of three kitControl objects - Maximum, Minimum, and Average - will all go to Nan if any of its inputs are Nan.
TAC IA Series
I/A Series G3 (Niagara) station
The internal logic of these blocks is set to pass Nan through if all inputs are not valid for comparison.
There are two potential work-arounds:
  1. Pass the inputs through some intermediate logic to ensure that a Nan value is never passed to the Minimum, Maximum, or Average blocks. Null values are valid and will allow the internal logic of the block to proceed.
  2. Use the MinMaxAvg block instead. It is located in the kitControl > Util folder. The internal logic of this block will ignore Nan inputs.
  • TAC IA Series
  • 6513