Niagara G3: Import existing ENC PxViews into an ENS

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Niagara G3: Import existing ENC PxViews into an ENS
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116873_brid
    sesa116873_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1229 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Niagara G3: Import existing ENC PxViews into an ENS

Picard Product_Support
‎2018-09-06 01:21 PM

Issue

Does Niagara G3 provide a way of importing existing ENC PxViews into an ENS? 

Environment

Niagara G3 version 3.5 or later

Cause

Importing existing ENC PxViews into an ENS is a time saving process.

Resolution

Niagara G3 does provide a way of importing existing ENC PxViews into the ENS with the use of exportTags, specifically PxViewTags.

  1. Open the exportTags in the Palette
  2. Drag and drop the SupervisorExportTagNetworkExt to the NiagaraNetwork of the ENS (server).
  3. Drag and drop the SubordinateExportTagNetworkExt to the NiagaraNetwork of the ENC.
  4. Enable the joinProfile in ENC:
    1. Expand the NiagaraNetwork of the ENC 
    2. Expand the ENS’ station.
    3. Double-click on the Join Profile and select Enable - Save.
  5. Setup the ENC’s PxViex File Structure:
    1. Expand Files Folder in the ENC and then expand joinProfile
    2. Expand ENS_profile.bog file and then expand niagaraStation
    3. Double-click the Points folder (The ENC’s PxViews will be setup here)
    4. Right-click in the ViewPane and select New Folder
      • You may want to give the folder the same name as the PxView being exported
      • The Folder structure should be the same PxViex folder structure as in the ENC’s PxView structure.
      • Add folder for each PxView to be exported to the ENS
    5. Right-click on ENS_profile.bog and Save.
  6. Placing PxViewTags in PxViews
    1. PxViewTags are placed in each PxView being exported to the ENS.
    2. From the Palette, open exportTags and expand the Extensions folder
    3. Drag and drop a PxViewTag into the ENC’s PxView folder to be exported
      • Configure each PxView’s Property sheet to point to the folders you created under Points in the ENS_profile.bog file.
      • Double-click on the PxViewTag to set its properties
      • For Supervisor Station, select ENS from the drop-down menu. - Save
      • For Station Slot Path, click on the folder to display the “Select Parent Target” window.
      • Expand NiagaraStation and then expand Points. 
      • Select the corresponding PxView Folder and click OK
      • For Px View, select the PxView to be displayed
      • Click Save to save changes.
    4. Repeat steps for each PxView being exported to the ENS
  7. Do a Join to export PxView to ENS
  8. Once the above is setup a join can be performed.  A join can be accomplished in two ways.
    1. Join #1
      • Expand the NiagaraNetwork of the ENC
      • Right-click on SubordinateExportTagNetworkExt, select Actions and then Join
    2. Join #2
      • Expand the NiagaraNetwork of the ENC and expand the ENS station
      • Right-click on Join Profile, select Actions and then Join

If everything was configured correctly, messages stating that both the Supervisor and Subordinate joins were successful will be displayed. If all goes well, then the ENC’s PxViews should appear in the Point folder of ENC under the ENS’ NiagaraNetwork.

Notes:

There were no provisions for importing the nav file during development of the exportTags. The file structure will also change once the ENC station.bog file is loaded on the Supervisor.

For more detailed information on PxViewTags reference the NiagaraAX Export Tags Technical Document. This document is located in docs folder of the Niagara build root directory.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6074
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore