Niagara Controller Diagnostics and Debug Basics

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Niagara Controller Diagnostics and Debug Basics
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2938 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Niagara Controller Diagnostics and Debug Basics

Guinan RandyDavis Guinan
‎2023-03-07 03:28 PM

Issue

What diagnostic information is available within Niagara that can be sent to Product Support or acted on locally?

Product Line

TAC IA Series

Environment

  • I/A Series Enterprise Server
  • I/A Series Jace

Cause

Jace or Enterprise Server operating slow or specific problems are causing the need for debugging a station or platform

Resolution

There are several diagnostic tools available:

  1. Check the station Resource Manager

    Right-click on the station and select "Views - Station Summary"

    Jace_1.pngThis will open up a resource monitor page where you can check CPU and memory usage.  The CPU should not be consistently above 80%.  Spiking is common as the process is executing and completing tasks.  There are other things easily referenced here also.

    Jace_2.png

    Heap memory will vary as well.  It can slowly increase until a garbage collection cycle releases unused heap back to the pool.  You should never use more than 75% of the total available heap memory. Heap Memory is primarily used by station modules and java program objects, so if the memory usage is high, these 2 might be the main reasons

  2. Engine Hogs

    Jace_3.png

    Jace_4.png

    Jace_5.png

     

    1. Right-click on the station, and select "Spy".
    2. From the main view, click on "sysManagers".
    3. Click "engineManager" and then scroll down
    4. to find "Engine Hogs". Clicking Engine Hogs will open a list of the main components of the station and a column on the right-hand side will display the average execution time of the component. Review the top 10 or so and see if any are taking an extraordinary amount of time.  This can help to locate improperly executing objects.

    Jace_6.png

  3. Driver Poll Rates

    Drivers that are based on polling data, like BACnet when COV is not enabled, or Modbus constantly run commands to read data based on the fast, normal, and slow configured rates.  Open the Poll Service under the network the points are being polled on.

    Jace_7.png

    Looking at the property sheet of the driver, it is important to verify that the cycle time (1) for each rate (fast/normal/slow) is always equal to, or below the actual time configured (2) for that rate. The defaults are 1 second for Fast Cycle Time, 5 seconds for the Normal Cycle Time and 30 seconds for the Slow Cycle Time. Seeing a longer cycle time is usually an indication that the network is saturated with commands and may cause the Jace/Niagara controller to be slow with heavy use of controller resources.  There are several ways to correct this:

    • changing the polling rate

    • spreading the number of objects being polled at each rate, etc. In this example, all points (3) are in the "normal" bucket.

  4. Application Director console

    The "Application Director" (under "Platform") shows a live console output.  Open it by clicking the option under the platform

    Jace_8.png

    Copy the content of the Application Director, or "stream to file" to send the content to support. It will be essential to help the support engineer to understand the problems in the station. 

    Jace_9.png

  5. Add more debug information to the Application Director console

    You can add more granularity to the messages in the Application Director for a deeper look into possible issues. This can be accomplished in 2 different ways:

    1. Right-click on the station, and select "Spy". Then, select "logSetup" on the main view

      Jace_10.png

      From the list that appears, you can scroll and find appropriate topics to log and you can select at what level you want the information to appear.  This will add traffic to the application Director window so be careful how "fine" and how many logs you enable.  It might be good to consult with support before enabling these logs. example; bacnet.debug/finest if you select this box.

      Jace_12.png

    2. Debug Service

      Jace_11.png

       

      1. Select the "DebugService" from the station "Services"
      2. In the Log Category, type a few letters of the topic and scroll to find what you are interested in logging
      3. From the pulldown menu, determine the granularity of the log
      4. Click the plus
      5. Click "Save"

      Setting this logging and streaming the output to a file will allow information to be sent to support for better diagnostics if required.  Remember to set this logging back to "Default" when done so the Application Director is not overwhelmed with information when you are only trying to view normal station activity.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • RandyDavis23
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore