New priority level of an alarm object does not take place

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • New priority level of an alarm object does not take place
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Anonymous user
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1318 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

New priority level of an alarm object does not take place

Picard Product_Support
‎2018-09-10 11:50 PM

Issue

Changing alarm priority level in Workstation or Menta does not work even after a download.

Environment

  • Xenta 280/300/401 controllers under Xenta Servers
  • Vista Version before 5.1.8 (5.1.8 is included)

Cause

This issue only happens if having a free programmable controller (Xenta 280/300/401) under a Xenta Server (Xenta 5/7/913).

When updating the priority level information in Menta or Workstation, Xenta Server does not get updated which caused the old alarm information appears when the alarm is activated. 

Resolution

This issue will be solved in the future release of TAC Vista. Currently, the work around is:

Method 1:

  1. Right click on the free programmable controller which contains the alarm object that needs to be changed, then choose “Edit” to open Menta editor.
  2. Double clicking on the alarm block that needs to be changed. Change the priority level to a desired value.
  3. Change the alarm object block name to a different name. -->force Xenta Server to notice a change in the Menta.
  4. Save the Menta file and do a “commission and download” of the related controller in Workstation.
  5. Right click on the corresponding Xenta Server and do a download in Xbuilder.

Method 2:

  1. Right click on the corresponding Xenta Server and select “Edit” to open Xbuilder.
  2. Find the alarm object under Lonworks Network in the Network panel and select it.
  3. In the Property panel, change the priority level to the desired value.

NOTE: Though Method 2 may be a faster way to change the priority level, it will cause Xbuilder object does not match the Menta file which is not recommended.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 12073
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of