New Door Attributes KeyPadString and KeyPadCommand in ACX57xx

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • New Door Attributes KeyPadString and KeyPadCommand in ACX57xx
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa119747
    sesa119747
  • Carl_Slack
    Carl_Slack
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1137 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

New Door Attributes KeyPadString and KeyPadCommand in ACX57xx

Picard Product_Support
‎2018-09-06 02:38 PM

Issue

New Door Attributes KeyPadString and KeyPadCommand in ACX57xx

Environment

Information about the new door attributes and configuration helps users with the capability.

Cause

  • ACX57xx
  • Continuum V1.82

Resolution

New Door Attributes KeyPadString and KeyPadCommand in ACX57xx in latest versions of Continuum Requires versions of Continuum V1.82 or above and Rev 1.1xxxxx ACX

Entering an Input String at a Keypad for Use in PE Programs

From a keypad connected to an ACX2 door, you (the user) may also send additional data to the controller, which in turn passes it to a Plain English (PE) program for execution in an Andover Continuum control application. This capability enables you to use the keypad to send input to a PE program for any purpose.

For example:
A user can enter a string that a PE program uses to turn lights or fans on or off, or to control other HVAC equipment. A user can enter a string indicating the user’s purpose for entering an area. The PE program can capture this information as input to a PE program for tracking reasons for activity in a secure area. 

Handling String Input at the ACX2 controller

Before you can use the keypad for PE program input, you must create a Plain English program that processes the string entered at the keypad and returns a value to the system based on the entry. The ACX2 door
contains two attributes that are used by the PE program

KeypadString door attribute. Your PE program reads this attribute to obtain the content of the string entered at the keypad.

KeypadCommand door attribute. Your PE program sets this numeric value to provide feedback via the reader/keypad LEDs to the person entering the keypad code about the status of the operation. Other commands are
also sent to the door via the KeypadCommand attribute such as enabling or disabling Keypad Input.

Entering String Input from Keypad

The process for entering string input at a keypad has the following steps:

  1. The user presents a valid access card and/or PIN (if a PIN is required) to the door reader.
  2. The controller for this reader accepts the user’s credentials, and the door unlocks.
  3. Within three seconds of the door unlocking, the user enters two consecutive asterisks ( ** ) at the keypad to enter escape sequence mode.
  4. The keypad LED flashes slowly to indicate that it is waiting for input.
  5. The user enters a numeric string of up to 30 characters (not including the two asterisks), and then terminates the string with the pound sign (#).
    For example: **10# or **6986310#
  6. The door makes the string available to a PE program via its KeypadString attribute.

Entry Rules for String Input

The following rules apply to using a keypad connected to a door to enter string input:
 

  • After the door unlocks for a valid access, if more than 3 seconds elapse before the user enters two asterisks, the door exits escape sequence mode. The user must begin the process for string input again.
  • If a user enters more than 30 characters (not including the first two asterisks), the door detects when the 31st digit is entered. The door then replaces the 30th character with T to indicate Tamper, and sends the string to its KeypadString attribute (no # is needed). Subsequent characters entered as part of the string are ignored.
  • For example, if the user enters **123456789012345678901234567890123, the door sends 12345678901234567890123456789T to its KeypadString attribute.
  • The user can enter asterisks within the string if needed. These asterisks are converted to periods when sent to the door’s KeypadString attribute.
  • For example: 69*8*6310 is converted to 69.8.6310 when sent to the door’s KeypadString attribute.
  • If more than 4 seconds elapse between keystrokes, the door exits escape sequence mode. The user must begin the process for string input again.
  • If a user presents an access card to the card reader while the door is in escape sequence mode, the door exits escape sequence mode. The user must egin the process for string input again.

PE Feedback to the Door

After the PE program receives the string input and interprets its value, the PE program assigns an appropriate value to the door’s KeypadCommand attribute. One of the following values is transmitted back to the door
through its KeypadCommand attribute:

  • 0 - Disable keypad Input at the door.
  • 1 - Clear string.
  • 2 - Recognize the escape sequence entry (success).
  • 3 - Do not recognize the escape sequence entry (fail).
  • 255 - Enable keypad Input at the door.

NOTE: Clearing the string in the door using the Clear String command is recommended after each string input in escape sequence mode.

Based on the numeric value returned to the door through the KeypadCommand attribute, the PE program uses the reader LEDs to indicate to the user whether or not the string input is valid or invalid. The LED pattern to indicate valid/invalid entry is the same as the selected access control LED pattern used to indicate valid/invalid card and PIN entry.

Sample PE Program

The PE program in the following example is used to unlock a door for unrestricted access for the amount of time specified in the Keypad Input String. For instance, at the door, the user enters 100*3600, the "*" gets translated to "." (period) so the keypad input string contains 100.3600.

The program recognizes 100 as the door timed unlock code and 3600 as the time to unlock the door for (in seconds, 3600 is the number of seconds in an hour), thus entering 100*3600 at the keypad instructs the PE program to unlock the door for an hour.

'This program processes the 'Timed Unlock' keypad code (100) entered at a door's keypad 'The form of the code is 100.xxx where 100 is the command identifier and xxx is the amount of time 'to unlock the door for.
String Str
Numeric KypdCode, DrUnlockTime, SeparatorPos

Line Init
  Jetway1 KeypadCommand = 255 'Enable door for keypad input string
  Jetway1 KeypadCommand = 1 'Clear any previous keypad input string
Goto WaitForKypdCode

Line WaitForKypdCode
  'Wait here until something goes in the keypad string
  If len(Jetway1 KeypadString) > 0 then Goto ProcessKypdCode

Line ProcessKypdCode
  'The string should contain 2 fields separated by a period
  'Get the keypad code identifier which is to the left of the separator
  SeparatorPos = search(Jetway1 KeypadString, ".")
  Str = left(Jetway1 KeypadString, SeparatorPos)
  KypdCode =StrToNum(Str)

  'Now get the unlock time value which is to the right of the separator
  Str = right(Jetway1 KeypadString, (len(Jetway1 KeypadString) - SeparatorPos))

  DrUnlockTime = StrToNum(Str)

  'The only keypad code this program handles is the time unlock (100)
  If KypdCode = 100 and DrUnlockTime > 0 then Goto UnlockDoor Else Goto InvalidKypdCode

Line UnlockDoor
  Jetway1 KeypadCommand = 2 'Flash the valid access LED pattern to give

  'feedback that the code has been accepted
  Jetway1 TimeUnlock = DrUnlockTime 'Unlock the door for the time specified
  'in the keypad code
  Goto ClearStr

Line InvalidKypdCode Jetway1 KeypadCommand = 3 'Flash the invalid attempt LED pattern to give
  'feedback that the code is invalid
  Goto ClearStr

Line ClearStr
  Jetway1 KeypadCommand = 1 'Clear the keypad input string
  Goto WaitForKypdCode

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 3433
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore