Issue
Within the Network modem object, what settings are required/normal for both the alarm delay and dial parameters windows?
Product Line
TAC Vista
Environment
- Xenta 901
- Vista
- Modem
- Manual
Cause
Problem/tip using modem dial
Resolution
This depends on the desired functionality. One examples definitions for the TAC Xenta:
- Dial when priority 1 alarms have been tripped/reset/acked
- Dial when priority 2 alarms have been tripped/reset
- Dial remaining alarms only once per day when it is cheaper to dial
It always depends on the site requirements. One recommendation is to use at least 5 minutes delay before dial up.
Please read the TAC Xenta 901 Handbook.