Network bandwidth consumed by a 511/911 LTA.
  • Network bandwidth consumed by a 511/911 LTA.
  • SESA116857
    SESA116857
‎2018-09-06 03:05 PM
What is the network bandwidth caused by a 511/911 LTA?
  • Xenta 511, 911
  • 911 Communication Port
While the maximum is rarely consumed this number should assist in conversations with IT departments for worst case scenarios and troubleshooting the Ethernet network.
  • The Ethernet bandwidth consumed by a single Xenta 511/911 LTA can range from 0 - 80 kb/s depending on network load.
  • 80kb/s is the fastest that the Neuron transceiver can communicate on the LON network.
  • 2038