Issue
Digital SAT outputs are not available when using the EBO MN-HPFC object
Product Line
TAC IA Series.
Environment
- I/A Series Network 8000 MN-HPFC
- Building Operation Automation Server Premium
- Building Operation Automation Server
Cause
The standard MN-HPFC device object in EBO cannot be used when the device was previously configured for Satellite Mode used in a Network 8000 system or R2 integration.
Resolution
Use the MN:MicroNet 2000 Generic object to interface to an MN-HPFC when configured for satellite mode. This object provides a set of generic inputs and outputs that map over to the satellite controller points. See the attached MN-HPFC Reference Manual that details the inputs and outputs starting on page 6-11.