Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Network 8000 LNC-100 cannot communicate to LON devices but can be accessed with WorkPlace Tech or LON commissioning tool

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Network 8000 LNC-100 cannot communicate to LON devices but can be accessed with WorkPlace Tech or LON commissioning tool
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2322 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Network 8000 LNC-100 cannot communicate to LON devices but can be accessed with WorkPlace Tech or LON commissioning tool

Picard Product_Support
‎2018-09-07 03:30 AM

Last Updated: Crewman ContentModerator ‎2025-10-15 03:38 AM

Issue

A Network 8000 LNC-100 cannot communicate to LON devices under it even though all the devices can be accessed with WorkPlace Tech or a LON commissioning tool.

Product Line

TAC IA Series

Environment

  • NETWORK 8000 LNC-100
  • LON devices
  • WorkPlace Tech

Cause

If the LON network is known to be good and otherwise functioning, this issue indicates a problem with the LON interface in the LNC-100. This is typically caused by accidentally attempting to commission the LNC-100 using LonMaker or other LON commissioning tool.

Attempting to commission the LNC-100 will result in its LON interface being set into a network state called HARD - OFFLINE.

Resolution

The condition can be corrected using the Echelon NODEUTIL program to set the interface network to the required CONFIGURED - ONLINE state.

NodeUtil can be downloaded from The Exchange Download Center.

After downloading NodeUtil to your computer, open a command prompt window and launch NodeUtil in that window.  After launching NodeUtil, perform the following steps to correct the problem.

  1. Press the F key to execute the Find function.  This will browse the connected LON network for all attached LON devices.  In the list of found devices, the LNC-100 will be identified with the program id "C 1 11.0A".
  2. Press the G key to execute the Go To Device function.  Enter the device number of the LNC-100 (program ID "C 1 11.0A") as displayed in the list of discovered devices.  The device menu will then be displayed.
  3. Press the S key to display the status of the device.  Typically 17 lines of status information are displayed followed by the "Device Status" menu.  Press Y to clear the error status.  The "Device State" line will usually show a state of either Configured, Off-line or Hard, Off-line.
  4. Press the  M key to change the device mode and state.
  5. After selecting the M command, the list of mode options is displayed.   Press the S key to select the State menu.
  6. The list of State options will be displayed.  Press the C key to set the device to the Configured state. A status message will be displayed followed by the DEVICE prompt.
  7. Press the M key again to display the Mode options then press N to set the device into the OnLine mode. A status message will be displayed followed by the DEVICE prompt.
  8. Press the S key again and verify that the Device State is now Configured, On-line.
  9. Press the D key to display the domain address table of the LNC-100.  One or two lines of device domain address information will display.  If two domain addresses were defined in the SYS: SIM block of the device, two lines of information will display, otherwise only one line will display.  Verify that the address information (Subnet, Node and Domain ID) are as set in the SYS: SIM block.
    The data entered for Domain0, Subnet0 and Node0 will be displayed on the Index 0 line.
    The data entered for Domain1, Subnet1 and Node1 will be displayed on the Index 1 line.
  10. Press the E key to exit the Device level and press the E key a second time to exit the program.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 3821
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore