Network 8000 HOST will not boot up, message "Unrecoverable error has occurred"

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Network 8000 HOST will not boot up, message "Unrecoverable error has occurred"
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa119747
    sesa119747
  • Product_Support
    Product_Support
  • SESA113595
    SESA113595

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1511 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Network 8000 HOST will not boot up, message "Unrecoverable error has occurred"

Picard Product_Support
‎2018-09-06 02:41 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-10-07 08:25 AM

Issue

Network 8000 HOST will not boot up, message "Unrecoverable error has occurred."

In some cases where the HOST loses power or is shut down without exiting properly, it will not boot up, and displays the following series of messages:

"Strong possibility that 3:/DMC.fmon / 011 has lost data.
** ERROR** In Shell call to fcompress to Routine error –1.
** ERROR** In Routine rebuild_fx_file error -14.
** ERROR** In Call to routine rebuild_db_file.
** ERROR** Unrecoverable error has occurred."

Product Line

TAC IA Series

Environment

Network 8000

Cause

Host was not properly shut down.

Resolution

To correct the problem, login to the QNX operating system and perform the following steps. QNX commands are enclosed in angle brackets, < cmd >. Type just the command, not the brackets, followed by ENTER.
See the HOST 8000 Troubleshooting Guide, F–26369, for more details on QNX commands and syntax.

  1. Check disk space, < files 3:/ >, note results, if less than 90% full, no problem.
  2. Check for busy files, < files 3:/ +b >, note results.
  3. Check for busy directories, < files 3:/ +d +b >, delete the 3:/tmp temporary directory, < zap 3:/tmp >. Should be prompted “file zapped”.
  4. Check the 3:/DMC.fmon directory, delete file new.f if it exists.
    1. Change directory, < cd DMC.fmon >.
    2. Verify change of directory, < pwd >,should be “3:/DMC.fmon”
    3. List contents of directory, < ls > ( lower-case L, not the number 1).
    4. Delete file new.f if it exists, < zap new.f >, should see “file zapped”.
  5. Delete the 011 file group, as follows:
    1. < zap 011.f >, should see “file zapped”.
    2. < zap 011.k >, should see “file zapped”.
    3. < zap 011.x >, should see “file zapped”.
    4. Verify file deletion, < ls > ; 011.f, 011.k, and 011.x should be gone.
  6. Recreate the 011 file group, as follows:
    1. < fconstruct 011 >
    2. < kconstruct 011 >
    3. Verify files have been rebuilt, < ls >; contents should include 011.f, 011.k, 011.x as well as the 021 and 054 files.
  7. Reboot the system, it should now boot all the way to the white Barber-Colman login screen.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 3283
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore