  • Why the Netcontroller 9680 can't be connected via Hyperterminal.
  • How to commission the NC2 and ACX2 (5720/5740)
  • Hyperterminal
  • NC2
  • ACX2
  • 5720
  • 5740
The Netcontroller 9680, usually called the NC2, does not have a Hyperterminal interface in which to commission the controller.
To commission the NC2 and the ACX2 please follow the directions below.
Note: Check with your system administrator for assistance.
  1. Disable the DHCP Services on your PC.
  2. Disconnect your computer from the network and set your IP address to 169.254.1.2 and your subnet mask to 255.255.0.0.
  3. Using a CAT5 cable (straight-through or crossover), connect the PC Ethernet port to the ACX 57xx Ethernet port.
  4. Run your web browser, then go to URL: http://169.254.1.1 to display the Andover Continuum Embedded WebServer page in the ACX 57xx Series controller.
  5. Select Controller Configuration from the WebServer page.
  6. Log on using the default Andover Continuum user name and password.
  7. Enter relevant configuration parameters on the WebServer Configuration web pages.
  8. After entering the parameters, click the Commit Changes/Restart Controller button on the WebServer page. (Restore the PC, and connect the controller to the network when it reboots.)