Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

NPRs - Solution information for IT professionals.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • NPRs - Solution information for IT professionals.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa139513
    sesa139513
  • SESA128071
    SESA128071
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1185 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

NPRs - Solution information for IT professionals.

Picard Product_Support
‎2018-09-06 03:11 PM

Issue

NPRs - Solution information for IT professionals.

Environment

I/NET site with a network

Cause

Is there information for the site IT Professional concerning NPRs

Resolution

The I/NET control network, on which the NPR is a component, makes exclusive use of UDP/IP packets. All retry, the control network applications layer handles timeout, and other packet transfer reliability. The maximum packet data component size is 140 bytes. The maximum UDP/IP packet size, including MAC and IP headers, is 186 bytes.

Most control network transactions occur in the following four sets of packets: Transmission packet, Acknowledge packet, Response packet, and Response-Acknowledge packet. This is true for all transaction types including manual operator control actions initiated from I/NET, controller software downloads, and trend data uploads. Three control network packet transaction types occur periodically and are formed as a set of two packets. These transactions are for node to node (on the control network) supervision, global data point distribution, and message (alarms, transactions) distribution. This two-packet set is constructed of a Transmission packet and a Response packet. Node-to-node supervision occurs every 15 seconds.

Global data point and message distribution occur at random intervals depending on the operator settings for those events on the control network. Acknowledge and Response-Acknowledge packets are 64 bytes in length. Transmission and Response packets will vary in length from 64 bytes to 186 bytes. The data content of the UDP packets is proprietary to TAC control networks. Critical configuration packet transactions between TAC control network machines use private key encryption to protect the data content. All other packet data contents are not encrypted.

The highest Ethernet network utilization will occur during an I/NET host PC to NPR software restore action. This is the only sustained network activity where transmission packet sizes are filled to the maximum of 186 bytes. It is also the only control network activity that will generate a continuous transmission data stream. Network utilization during activity will be between 2 and 3 percent. To validate this statement, the Triticom Landecoder32 Ethernet monitor was used to observe network activity during the software restore process.

Broadcast UDP/IP packets are NOT utilized by the control network applications. The only Ethernet broadcasts that will be used are standard ARP broadcasts for normal MAC to IP address resolution.

The NPR requires a static IP address assignment.

The control network makes use of logical port number 50069 as the transmission packet destination.

The NPR exposes an SNMP agent that will provide SNMP managers access to the standard MIB2 network variable set.

The NPR exposes a limited Telnet service that provides connecting clients access to control network specific debug information such as the application layer routing table a well as the IP stack routing table and ARP cache.

The NPR operates at 10 Mbs and communicates at half duplex.
 

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 1758
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore