Multiple Menta Variable errors in the TAC Xenta 700 error log
  • Multiple Menta Variable errors in the TAC Xenta 700 error log
‎2018-09-11 12:58 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:52 AM
Multiple Menta Variable errors in the TAC Xenta 700 error log and, if running TAC Vista, also in the event log
TAC Vista 5.1.7
TAC Xbuilder 5.1.7
Xenta 700 system software (firmware) 5.1.7-51 (5.1.7-SP2) or 5.1.7-52
When releasing TAC Xenta 700 5.1.7 SP2, an error was introduced to the firmware if the ERROR block
exists in the TAC Xenta 700 Menta object.
The error you see in the Xenta 700 error log will look similar to the following:
138   2013-01-15 14:29:18 minor   menta menta           138  alarmstate.anyun
      Menta: Variable error   (Error#:62466)
This issue has been fixed in the TAC Xenta 700 5.1.7 SP3 release, available for download at Exchange Extranet.
After a successful update the firmware version will read 5.1.7-53.
  • 12332