Multiple Email Addresses for Email Notifications or Alarm Recipients

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Multiple Email Addresses for Email Notifications or Alarm Recipients
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Hernan_Urueña
    Hernan_Urueña
  • DavidFisher
    DavidFisher
  • sesa139513
    sesa139513
  • HenrikTarpgaard
    HenrikTarpgaard
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4682 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Multiple Email Addresses for Email Notifications or Alarm Recipients

Picard Product_Support
‎2018-09-06 12:10 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-18 10:40 PM

Issue

How to put in multiple email addresses for emailing from Email Notification

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server (ES)
  • Building Operation Automation Server (AS)

Cause

It is often required that alarm notifications to be sent to multiple stakeholders simultaneously for timely response.

 

Best Practice: Use an email distribution list (DL) or group on your mail server and reference that DL address in EcoStruxure Building Operation. This simplifies recipient management and reduces maintenance overhead.

Resolution

 

  1. Open Email Setup in WorkStation (or Project Configuration Tool) > navigate to Notification > Configure Email.

  2. In the “To” field, enter multiple addresses using this syntax:

    user1@domain.com;user2@domain.com;user3@domain.com
    
    • Separate addresses with semicolons (;) and do not include spaces.
    • Alternatively, select user accounts or groups to manage recipients dynamically.
    • Ensure each user account exists on the BMS server and has proper alarm handling permissions.
  3. Configure SMTP settings (server, port, SSL/TLS, credentials) under right click  Server Properties > Email.

    Hernan_Uruea_2-1763531640111.png

     

    Hernan_Uruea_1-1763531468547.png
  4. Choose how notifications appear:

    • Inline email text, or
    • As an attachment (TXT, XLSX, or PDF), with dynamic filenames if needed.
    • Example: user1@gmail.com;user2@gmail.com;user3@gmail.comHernan_Uruea_0-1763531337230.png
  5. If email delivery fails, Building Operation generates a system information alarm indicating SMTP issues.

Recipient Limit Note:
EcoStruxure Building Operation does not impose a hard limit on the number of email addresses in the “To” field. However, your SMTP server or email provider may enforce limits (e.g., Microsoft 365 allows 500 recipients per message; Gmail and ISPs have similar restrictions). To avoid delivery failures, use distribution lists or user groups for large recipient sets.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 8308
  • HernanUruena25
  • smtp
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore