Issue
Moving a Converted I/NET graphic for the ES level integration of I/NET to the AS level of Integration to I/NET
Environment
StruxureWare
TGML
I/NET
Cause
As sites expand, controllers that are currently integrated to StruxureWare using the Enterprise server may be connected to the USB interface to the Automation Server. It is possible for these relocated controllers to continue to use the same graphics.
Resolution
- Recreate the exact folder location of the graphic on the AS. For Example, if the graphic is currently on the ES\INET Interface\INET Graphics folder, the user should create an INET Interface\INET Graphics Folder on the AS
- Copy the Graphic on the ES
- Paste the Graphic on the AS
- Clean up any bindings. Any I/NET objects that were re-named after the initial conversion may need to be manually re-bound. Links between graphics may also need to be re-bound.