Issue
Modify occupied cooling and heating (nciSetPts) variables on Viconics VT7652 LON stat, but changes are not transmitting to thermostat.
Have a DynamicCmd object linked up and can write the values in the DynamicCmd but they don’t ever change in the thermostat and they don’t show up in the nvoEffectSetPt variable.
Environment
VT7200 LonWork series
VT7300 LonWork series
VT7600 LonWork series
Cause
Setup of limits
Resolution
Check the HeatMaxSetpoint and CoolMinSetpoint limits found in the nciCfgRtuHP ( Vt76Pir properties).
When a change that is outside of the limits, it will take the request but will not transmit change down to the thermostat.