Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Modbus communication between the ICP 7188 and the Caterpillar genset SCM module.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Modbus communication between the ICP 7188 and the Caterpillar genset SCM module.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Anonymous user
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1428 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Modbus communication between the ICP 7188 and the Caterpillar genset SCM module.

Picard Product_Support
‎2018-09-07 02:27 PM

Issue

The modbus RTU communication from the ICP 7188 and the Caterpillar SCM module stops communicating after the genset hand off auto switch has been placed not in auto.

Environment

ICP 7188

Modbus RTU

Caterpillar SCM Module

Cause

When the Caterpillar genset hand of auto switch is placed not in auto for monthly genset tests or to manually run the generator the SCM module on the generator senses this state change and sends a "wait" command on the modbus network that the ICP 7188's modbus driver can not handle.

Resolution

There are two resolutions to this problem depending on what version of the modbus driver running in the ICP 7188.

  1. If the modbus driver dated 2-16-2001 is being used in the ICP, the only resolution will be to power cycle the ICP after the genset has been placed in "not in auto". This will re-initiate the communication on the modbus network. This modbus driver version does not have the capabilities to handle the 'wait" message from the SCM module.
  2. Upgrade to the final modbus build for the ICP 7188 dated 3-4-2005. This driver has the ability to receive the "wait" command from the SCM module on the modbus network.

To upgrade the ICP 7188 to the final modbus build, simply place the ICP7040.exe, SP7040.def, and SP7040.exe files from the attached.zip file in the linkterm directory, and redownload the ICP.

 

NOTE: The ICP7188 is no longer officially supported by Schneider Electric as the gateway device for I/Net integration efforts. The Xenta 913 is the official replacement for the ICP 7188 when doing third party integration to an I/Net system.

Labels (1)
Labels:
  • TAC INET
Attachments
SP7040.zip
Tags (1)
  • Find more articles tagged with:
  • 5000
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore