Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Miscellaneous fixes in Workplace Tech 5.5 and 1.4 controller firmware.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Miscellaneous fixes in Workplace Tech 5.5 and 1.4 controller firmware.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa119747
    sesa119747
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1201 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Miscellaneous fixes in Workplace Tech 5.5 and 1.4 controller firmware.

Picard Product_Support
‎2018-09-06 02:55 PM

Issue

Miscellaneous fixes in Workplace Tech 5.5 and 1.4 controller firmware.

Environment

  • Workplace Tech 5.5
  • 1.4 controller firmware

Cause

Require detail on what miscellaneous fixes in Workplace Tech 5.5 and 1.4 controller firmware.

Resolution

Visio 2003 generates an error and crashes when attempting to save a Visio drawing outside of the WPT environment. 

In WPT, the existing application tab in the add application to project dialog area is unable to open and add an existing application drawing.

The MNB-1000 will reset in response to a read or write request for the profile_name property or background BACnet object.

Cannot read/write background BACnet AO, Floating Actuator or PWM object in MNB-1000.

AppLED stops updating in the MNB-1000.

Sometimes an unsupported property response when reading BI object name in the MNB-1000.

Power up delay object did not work correctly in the MNB-1000.

Single and sequence loops incorrectly calculate output.  This issue was found when single and sequence loops were set up with large throttling ranges and had a small positive deviation from setpoint. During these conditions, the output of the loop would intermittently go to 100% output and then return to normal operation. This issue applied to MNB-1000, MNB-300 and MNB-Vx controllers.

Interstage delay fails after power cycle causing outputs to come on after controller power cycle of MNB-1000.  Dual delay object may be in incorrect state after controller power cycle of MNB-1000.  There was an issue found where the Dual Delay had a 50/50 chance of coming up in the correct state after a power cycle. 

Control object RAM not initialized correctly after a download of an application.

Floating Actuator object may oscillate at 22.22 and 66.77% output. This issue was reported in MNB-1000, MNB-300 and MNB-Vx.

BACnet flow balance values except BoxFlow can sometimes show error. 

COV increment property of the VAV Actuator object does not take effect.

Using the MN-Sx sensor to change temperature calibration does not work when temp calibration is set to NA from WPT or a BACnet tool and can lock up S-Link communications for MNB-300 and MNB-Vx controllers

Overridden and Out_Of_Service flags for PWM and momentary SS objects not previously supported in MNB-300 and MNB-Vx controllers.

COV increment property not previously supported for BI count output of MNB-300 and MNB-Vx controllers.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 2723
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore