Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Minimizing network traffic in Infinity controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Minimizing network traffic in Infinity controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Dave_Shore
    Dave_Shore
  • DavidChild
    DavidChild
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1942 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Minimizing network traffic in Infinity controllers

Picard Product_Support
‎2018-09-06 12:37 PM

Last Updated: Sisko DavidChild Sisko ‎2020-03-09 06:54 AM

Issue

Minimizing network traffic when sharing data between Continuum Infinity controllers

Product Line

Andover Continuum

Environment

  • CyberStation
  • All CXs
  • All i2s, Infinet Controllers

Cause

Accessing a remote point’s attribute other than value is a point to point operation that generates extra traffic.

Resolution

Continuum controllers implement an Import/Export strategy in order to minimize network traffic when accessing the value of a point in a remote controller; this is in some ways similar to BACnet COV.

When the value of a remote point is referenced in a PE program the system takes care of making sure the owner of the point sends the value to the subscriber(s) via the Import/Export system ONLY when the value changes.

Consider the following PE program line…

MyNum1 = RemoteCX\Num1

If a looping PE program sits on the line above no extra traffic is generated as the PE program gets the value of RemoteCX\Num1 from its local Import/Export table, information only goes on the wire when RemoteCX\Num1 changes value.

The only problem here is that the Import/Export system ONLY works for the VALUE attribute, any other attribute requested from a remote object results in a point to point message on the network to obtain the requested attribute value.

Consider the following PE program line in a CX controller we will call LocalCX

NyNum1 = RemoteCX\Num1 size

If a looping PE program sits on the line above a number of point to point messages would go on the wire every time the line executes. If there are many requests for attributes on remote objects a degrading in communications could take place.

One way to avoid degrading communications as explained above is expose the value of the attribute in question by placing it in the value of a numeric object.

Example:

In RemoteCX create a numeric point (Num1Size) to hold the size of Num1 and use a PE program to set Num1Size

Then the program in LocalCX will look like this…

NyNum1 = RemoteCX\Num1Size

Since the program is now going after the value attribute of Num1Size the import/export system will be used instead of point to point.

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 7406
  • DavidShore20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore