Migrate from custom installed Microsoft SQL Server 2000 to custom installed Microsoft SQL Server 2005

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Migrate from custom installed Microsoft SQL Server 2000 to custom installed Microsoft SQL Server 2005
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Benji
    Benji
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1505 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Migrate from custom installed Microsoft SQL Server 2000 to custom installed Microsoft SQL Server 2005

Picard Product_Support
‎2018-09-07 02:30 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-11-03 06:22 AM

Issue

Migrate from custom installed Microsoft SQL Server 2000 to custom installed Microsoft SQL Server 2005

Product Line

TAC Vista

Environment

  • Microsoft SQL Server 2000
  • Microsoft SQL Server 2005

Cause

When you upgrade from Vista 4.3.0 - 4.5.0 to Vista 5.x you can continue to use the SQL Server 2000, but as the security and performance is better in SQL Server 2005, you would want to upgrade. There are some things that are important before you upgrade. You should of course take a backup, but there are also some other things you should have in mind.

  1. If you want to have the same instance name on the SQL Server 2005 as you have on the SQL Server 2000, you must have two different PCs.
  2. The SQL Server 2000 should be SP4
  3. The SQL Server 2005 should be SP2
  4. The SQL Server 2005 should be minimum “Standard” version

Resolution

Always remember to update from TAC Vista 4.5.0 to TAC Vista 5. This means that you have to update to TAC Vista 4.5.0 if you are currently running eg. TAC Vista 4.4.1.

Procedure

  1. Upgrade TAC Vista to 5.x, and have it connect to the existing database on SQL Server 2000.
    • Check the existing SQL setup in TAC Vista Server Setup.
    • Uninstall TAC Vista 4.5.0.
    • Restart the PC.
    • Install TAC Vista 5.
    • In the installation procedure, type in the SQL credentials you checked earlier.
  2. Stop TAC Vista Server and DSS Writer.
    • To view installed services go to Start > Run > services.msc.
    • If TACOS is running as a service, stop it in the services and set it to disabled.
    • Stop the “TAC DSS Writer service” and set it to disabled.
  3. Assure that the SQL Server Agent is started on both the SQL Server 2000 and the SQL Server 2005.
    • This can be checked in Start > Programs > Microsoft SQL Server 2005 > Configuration Tools > SQL Server Configuration Manager.
  4. Start the “SQL Server Management” on the PC where SQL Server 2005 is installed.
    • This is the management tool that comes with SQL Server 2005
  5. Connect to both the SQL Server 2000 and SQL Server 2005.
    • The connect button is located in the upper left corner.
    • Login using either windows or SQL authentication.
  6. Right click the Vista log database on the SQL Server 2000, select all tasks and copy.
    • Follow the instructions in the wizard, and copy the database to the SQL 2005 Server (VERY slow process).
  7. Configure TAC Vista to connect to the copied database on the SQL Server 2005
    • Go to the SQL setup in TAC Vista Server Setup and have it connect to the DB on the SQL 2005 Server in stead of the SQL 2000 Server.
  8. Start the DSS Writer
    • Go to Start > Run > services.msc
    • Set the “TAC DSS Writer service” to automatic and start it.
  9. Start TAC Vista
    • If TACOS is installed as a service, set it to automatic and start it.
    • Otherwise, just start the TACOS application.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 3568
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore