Menta blocks RI and TSCHI won't work correctly together in simulation mode
  • Menta blocks RI and TSCHI won't work correctly together in simulation mode
  • HenrikTarpgaard
    HenrikTarpgaard
‎2018-09-10 06:21 AM
  • In Menta simulation mode, when changing the RI block (using the button on the left hand side), the TSCHI will get the same value
  • When changing the TSCHI block, nothing will happen at all
TAC Menta
Xenta 701, 711, 721, 731
This happens due to a bug in TAC Menta.
Create the TSCHI block before the RI block (this issue will only occur when the RI block is created first).
Please note the this issue only affects simulation mode of Menta, you won't notice it  when the project is downloaded to the device.
  • 7260