Menta Divide by Zero Error and Symptoms

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Menta Divide by Zero Error and Symptoms
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1686 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Menta Divide by Zero Error and Symptoms

Picard Product_Support
‎2018-09-06 01:27 PM

Issue

  • If the result of a divide by zero is sent to a physical AO, Vista Workstation will display this value as -2. The physical output, however, will be sending out the maximum specified voltage (default 10V).
  • In Menta simulation mode, if a divide by zero scenario is simulated, the following error will pop up:



    tam32
    Division by zero
  • Connected to a controller viewing live Menta, a divide by zero equation will result in a displayed value of 1.#QNAN. All subsequent equations using this value will also output 1.#QNAN.

Environment

  • Xenta programmable controllers
  • Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B
  • Menta

Cause

Division by zero results in an invalid value that is interpreted differently by the controller's physical outputs, the Menta application, and the Vista Workstation. The application will continue to run, but any output affected by the invalid value will not act as expected.

Division by zero is not usually intentional (there's no equation that says "A/0"). Instead, it is usually the result of an unforeseen sequence of events where complex equations result in a 0 in the denominator of an equation, and simulations did not ever produce this unique situation.

Resolution

To troubleshoot whether a divide by zero is occurring:

  1. The best solution is to connect live to the controller with a serial cable and watch the live Menta. Look for any values that read 1.#QNAN and trace it back to the source.
  2. If live Menta is no available, the simulation mode can be helpful. Recreate the scenario as best as possible with all inputs set to the real life instance.

To prevent a divide by zero error:

Never allow an equation to write to the denominator of a division equation without programming divide by zero prevention.

  1. Add an expression block prior to the division equation that says "if the value is zero, then output a safe value"
  2. Add a max block to the input that compares the value with 0.0001, so that a zero will never pass through.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5990
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of