Max number of HTTP sessions in Xenta 5/7/9xx functionality

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Max number of HTTP sessions in Xenta 5/7/9xx functionality
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1567 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Max number of HTTP sessions in Xenta 5/7/9xx functionality

Picard Product_Support
‎2018-09-10 12:43 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:52 AM

Issue

In XBuilder there is a setting called "Max number of HTTP sessions" that can also be found using the web interface by navigating to Configuration > Servers > HTTP Server. What does this setting do? Does it limit the number of users who can log in simultaneously?

Environment

  • Xenta Server
  • Xenta 511, 527, 555, 701, 711, 721, 731, 913
  • XBuilder

Cause

This setting is somewhat vague and is sometimes believed to be a limit on the number of simultaneously logged-in users.

Resolution

The Max. number of HTTP sessions is set to a default value of 15 and can be set to anywhere from 10-20. This setting does not limit the number of simultaneously logged in users, however.

The TAC Xenta Server - TAC Networks Technical Manual explains this setting as follows:

HTTP
The Xenta Server is an HTTP (Hypertext Transfer Protocol) server. Several users can view the web pages at the same time, but they are limited by the number of HTTP sessions allowed.

  • Max. simultaneous HTTP sessions, choose a number from the list. The default setting is 15. Several users can view files at the same time.

What is an HTTP Session?
Internet Explorer is an HTTP client, sending requests to the Xenta Server. The HTTP server in the Xenta Server receives the request and, following any necessary processing, the requested file is returned. An HTTP session is the connection that exists during data communication between the web browser and the Xenta Server. The session ends when all the data has been received.

Rules of Thumb
Each web page (values page, alarm page, and the graphics page), sets up a full HTTP session.
When loading a web page, a number of sessions may be used simultaneously, depending on the number of sessions available.

Labels (3)
Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5791
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.