Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Maintaining precision in meter readings when displaying in Xenta Server or Vista

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Maintaining precision in meter readings when displaying in Xenta Server or Vista
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa115370
    sesa115370
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1721 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Maintaining precision in meter readings when displaying in Xenta Server or Vista

Picard Product_Support
‎2018-09-06 12:14 PM

Issue

Many electrical power meters provide a high resolution Modbus or M-Bus output for cumulative parameters such as kWh, kVAh and kVARh.  This output can be displayed in Vista or on an Xenta Server web page, but the resolution can be degraded by inappropriate conversions in XBuilder and choice of display format.  This article shows how to maintain the full resolution of a meter reading from acquisition through to display on a Vista graphic or Xenta Server web page.

Environment

Xenta 511, 527, 555, 701, 711, 721 (5.1.5 up)

Xenta 731, 913 (all versions)

XBuilder

PM710

Cause

Applying scaling or connections in XBuilder, or processing in Menta, reduces the precision of a high resolution Modbus value to that of a Real or Float.

Resolution

The following comments refer to Modbus registers in the Schneider Electric PM710 energy meter, although many other meters deal with extended precision values in a similar manner. 

Acquiring Data from the meter:

1. If you want to maintain the full precision of the meter 'Real Energy, Total' reading, use register 4000 which is a 32 bit signed integer, representing scaled kWh. The scale factor is stored in register 4108 as a 16 bit integer and the two registers should be used in conjunction for display purposes. The maximum full precision value that can be displayed this way is: 2147483647 - 10 decimal digits - before the scale factor is applied.

2. An alternative to register 4000 is provided in register 1000, which is of type 'Float'.  This equates to the REAL type in XBuilder, so it already has only 21 bit precision. However, there is no need to scale it as the exponent is built in to the Float type.

Processing input in XBuilder:

3. For register 4000 in the device template, apply a gain of 1 and keep the converted value as INTEGER.  This will maintain the full 32 bit precision of the Modbus register.  If you apply any gain less than 1 or convert the value to a REAL, you will only end up with a 21 bit precision result.  This equates to a loss of 2 decimal digits approximately.

4. Avoid using Connection objects.  For example, a variable of type 'SNVT_elec_kwh_l' has theoretically the same precision as register 4000 in the PM710, so it would seem to be a direct conversion.  However, because you have to use a Connection object to link the two in XBuilder, the value is converted to a REAL internally and you end up with a 21 bit precision result.

5. Xenta Servers can provide full precision Modbus values for display in Vista. Create new Signal objects in the System pane in XBuilder and drag and drop the Modbus values from the Network pane onto the Signal objects.  The Signal objects will have the same precision as the original Modbus registers and are visible in Vista.

Displaying values in Xenta Server and Vista:

6. Value pages in the Xenta Server and TGML graphics pages in Xenta Server and Vista can display a 10 digit integer. In the case of item 1 above, all 10 digits will be accurate. In the case of item 2 above, only the most significant 8 digits will be accurate.

7. A value page in the Xenta Server will display a real as 8 digits plus exponent. However, only the 7 most significant digits will be accurate.

8. The object view in Vista will display a real up to 8 significant digits, with only the most 7 significant digits being accurate.  Vista will attempt to show this as fixed point 6.2 and no exponent.  If the actual value is too big or small for this format it reverts to 3 significant digits plus 3 digit exponent.

 

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 8164
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of