Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

MP-V/RP-V Air Flow reading 0 CFM

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • MP-V/RP-V Air Flow reading 0 CFM
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • DavidFisher
    DavidFisher

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
3707 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

MP-V/RP-V Air Flow reading 0 CFM

Administrator DavidFisher Administrator
‎2021-11-11 12:08 PM

Issue

MP-V Air Flow is reading zero flow despite the Velocity Pressure having a positive value.

Product Line

EcoStruxure Building Operation

Environment

  • MP-V-7A, MP-V-9A, RP-V-4A, RP-V-5A
  • Variable Air Volume Data

Cause

The Air Flow value is an internally calculated value based on the Velocity Pressure. There are a number of values involved in that calculation that could result in no flow.

Resolution

  1. Validate Variable Air Volume Data > Flow Balance Data > Rated box flow. The rated box flow defaults to 0 ft³/min in a new controller and must be replaced with the rated flow at 1.0inH₂O (provided by the box manufacturer).
  2. Compare Variable Air Volume Data > Velocity Pressure > Value to the Zero flow threshold. Any Velocity Pressure below the threshold will result in no flow. This threshold defaults to 0.008inH₂O.
  3. balanced-k-factor-flow-correction-factor.pngCheck Variable Air Volume Data > Properties > Balanced k-factor and Balanced flow correction factor. If either of these values are at 0, there will be no flow. These values cannot be directly written to and are only the result of a flow balance calculation. To get them to update:
    1. Go to Variable Air Volume Data > Flow Balance Data and record all balancing data (you will need to manually re-enter it later).
    2. Set all 7 balancing values to 0 - Rated box flow, Box/Hood measured maximum/intermediate/minimum
    3. Right-click on Variable Air Volume Data and Download
    4. Re-enter the valid balancing data. The balanced k-factor should now show a value close to the rated box flow and the balanced flow correction factor should show a multiplier ideally between 0.5 and 2.
      If the box has not been balanced and no valid balancing data is available, leave the minimum flow readings at 0 and enter the same value into both the hood and box maximums (for example, 1000 and 1000). This will result in a balanced k-factor equal to the rated box flow and a balanced flow correction factor of 1.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Was this article helpful? Yes No
67% helpful (2/3)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of