Issue
Cannot communicate to third party devices using the MODBus TCP XDriver or MODBus RTU XDriver.
Environment
- CyberStation
- ACX5740
- XDriver
- MODBus
- TCP
Cause
The MODBus TCP configuration point was not created
Resolution
Create the MODbus TCP configuration point following the guidelines in section 5.1.3 of the MODBus TCP guide