MNL-200 controller's analog output used as relay output
  • MNL-200 controller's analog output used as relay output
‎2018-09-11 03:48 AM
Last Updated: Crewman ContentModerator ‎2025-08-11 04:04 AM
Can the MNL-200 controller's analog output be used to turn a relay on and off?  Can you recommend a brand/model of relay?
TAC IA Series
I/A Series MNL Controllers
The application requires additional digital outputs
At 500 ohms and 20mA, the analog output produces 10 Vdc.  The voltage can go as high as11 Vdc by using a 550-ohm resistor instead.
A common brand and model is from Kele (model # KEL-RIBU1C) and it's available on iPortal.  The coil pulls in at 10 Vdc and drops out at 3 Vdc.  Click here for the datasheet.
  • TAC IA Series
Tags (3)
  • 13096
  • RandyDavis22
  • RIBU1C