Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

MNB-Vx actuator block output shows 'NaN' instead of a valid position

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • MNB-Vx actuator block output shows 'NaN' instead of a valid position
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Leo_Tantalo
    Leo_Tantalo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1886 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

MNB-Vx actuator block output shows 'NaN' instead of a valid position

Picard Product_Support
‎2018-09-11 02:53 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-07-30 06:34 AM

Issue

The output of the actuator block in a MNB-Vx sometimes shows 'NaN' (Not a Number) instead of a valid position. The only way to clear it is to drive it fully open or fully closed. The issue is intermittent and it is not specific to the same installed controllers. It appears on different controllers at different times.

Product Line

TAC IA Series

Environment

MNB-Vx

Cause

The actuator can be initialized to avoid displaying 'NaN'. The setting in the VAV actuator block is called InitMode. Here's a description of this setting from the WorkPlace Tech Engineering Guide Supplement (F-27356):

Abbreviation Configuration Property Description Range
InitMode Initialization Mode

Class: Enumeration - The initialization mode configuration property controls synchronization of the VAV object position output after a rest.

0 - No automatic synchronization of the position output. Synchronization occurs when normal control causes the actuator to drive full open or full closed.

1 - Actuator drives full closed after a controller reset to synchronize position output

2 - Actuator drives full open after a controller reset to synchronize position output

0-2

If InitMode = 0, and the actuator doesn't drive full open or full closed for a long period of time, the NaN value will continue to be displayed.

Resolution

Ensure InitMode is set to either 1 or 2 so that it synchronizes after a power cycle or database download.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 16460
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now