MNB-Vx actuator block output shows 'NaN' instead of a valid position
  • MNB-Vx actuator block output shows 'NaN' instead of a valid position
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-11 02:53 PM
Last Updated: Administrator DavidFisher Administrator ‎2019-07-30 06:34 AM
The output of the actuator block in a MNB-Vx sometimes shows 'NaN' (Not a Number) instead of a valid position. The only way to clear it is to drive it fully open or fully closed. The issue is intermittent and it is not specific to the same installed controllers. It appears on different controllers at different times.
TAC IA Series
MNB-Vx
The actuator can be initialized to avoid displaying 'NaN'. The setting in the VAV actuator block is called InitMode. Here's a description of this setting from the WorkPlace Tech Engineering Guide Supplement (F-27356):
Abbreviation Configuration Property Description Range
InitMode Initialization Mode
Class: Enumeration - The initialization mode configuration property controls synchronization of the VAV object position output after a rest.
0 - No automatic synchronization of the position output. Synchronization occurs when normal control causes the actuator to drive full open or full closed.
1 - Actuator drives full closed after a controller reset to synchronize position output
2 - Actuator drives full open after a controller reset to synchronize position output
0-2
If InitMode = 0, and the actuator doesn't drive full open or full closed for a long period of time, the NaN value will continue to be displayed.
Ensure InitMode is set to either 1 or 2 so that it synchronizes after a power cycle or database download.
  • TAC IA Series
  • 16460