MNB VAV Flow Balance data is stored separately from the application data
  • MNB VAV Flow Balance data is stored separately from the application data
  • Kim_Baze
    Kim_Baze
‎2018-09-06 01:22 PM
If a database is downloaded to the controller after the box has been balance will it lose the balance data?
TAC IA Series
  • All versions of MNB VAV controllers
  • MNB-V1
  • MNB-V2
In MNB VAV controllers the flow balance data is preserved in a different area of EEPROM than the application data.
Balance data in an MNB VAV controller is not affected by the downloading of its database.
  • TAC IA Series
  • 6044