Lowest correct measurement SPD310/SPD360
  • Lowest correct measurement SPD310/SPD360
  • SESA150559
    SESA150559
‎2018-09-06 12:31 PM
Choosing the correct range of sensor is important in order to provide the most accurate value.
SPD310
SPD360
Only the max value is specified for each range. How low is the lowest accurate value?
The reasonable minimum pressure in the 100Pa range should be equal or greater than 40Pa (typically), otherwise the max. error becomes bigger.
  • Field Devices
  • 7599