Creating and Using Lookup Tables for Resistive AI Devices in Sigma Controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Creating and Using Lookup Tables for Resistive AI Devices in Sigma Controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidChild
    DavidChild
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2307 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Creating and Using Lookup Tables for Resistive AI Devices in Sigma Controllers

Picard Product_Support
‎2018-09-06 01:37 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-04 11:01 PM

Issue

Sigma controllers require accurate interpretation of resistive analogue input (AI) signals. When using non-standard sensors such as 10k Type 2 or Type 3 thermistors, incorrect resistance values can trigger hardware alarms or result in inaccurate readings. A custom lookup table must be created to ensure proper operation.

Product Line

Satchwell BAS & Sigma

Environment

Satchwell BAS & Sigma UNC controllers

Cause

Sigma controllers interpret resistance values as a percentage of a 2V signal at the A/D converter. The default lookup tables are designed for specific sensor types (e.g., D?T range). When integrating other resistive sensors like 10k Type 2 or Type 3 thermistors, the controller may not recognize the input correctly, leading to hardware alarms or misread values. A custom lookup table is required to translate resistance values into valid input percentages.

Resolution

Step-by-Step Process to Create a Lookup Table

  1. Gather Sensor Data
    Obtain resistance values at various temperatures from the sensor’s datasheet

  2. Use the Sigma Calculation Formula

    R1*250 / R1+14700

    Where:

    • R₁ = Sensor resistance
    • 14700 = Resistor value on the AI card

    The circuit shown below is a typical example of an AI channel for a resistance input.

     

    CraigEl_0-1762325159472.jpeg

    To ensure the circuit resistance does not exceed 10kΩ, it is recommended to place a 10kΩ shunt resistor in parallel with the sensor.

  3. Create the Lookup Table Object

    • Enter the calculated input values into a new lookup table object in Sigma.
    • Ensure the table covers the full operating temperature range of the sensor.
  4. Assign the Table to the AI Object

    • Link the custom lookup table to the relevant analogue input object in Sigma.
  5. Download and Apply

    • Use Sigma System Setup and Diagnostics to build and download the new lookup table to the controller.
  6. Verify Operation

    • Check that the AI object displays correct temperature values.
    • Use programmable objects if additional formatting or scaling is needed.

Examples

  • Type 2 Resistances.pdf
  • Type 3 Resistances.pdf
  • Lookup Table Details

    • Column C: Raw sensor resistance
    • Column D: Controller input resistance with 10kΩ shunt resistor
    • Columns E & F: Example lookup table values (percentage of 2V signal)
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Attachments
Tags (3)
  • Find more articles tagged with:
  • 5550
  • CraigEllis25
  • DavidChild19
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore