LonWorks communication abilities of Xenta Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • LonWorks communication abilities of Xenta Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • SESA116857
    SESA116857
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1460 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

LonWorks communication abilities of Xenta Server

Picard Product_Support
‎2018-09-06 01:30 PM

Issue

What LonWorks data is accessible from a Xenta Server and what can the data be used for?

Environment

  • Xenta 500
  • Xenta 700
  • Xenta 900
  • XBuilder

Cause

There are different types of data accessible on a LonWorks network.

  1. TAC network variables / Public Signals - TAC proprietary communication for signals from Xenta programmable controllers
  2. SNVT - network variables available for bindings
  3. SCPT/UCPT - Configuration properties for LonWorks devices.
  4. UNVT - User defined SNVT.

Data accessible from a Xenta Server can be used in Xbuilder in multiple ways:

  1. Polling - value polled for use in graphics page, values page, alarm, trending, and scheduling.
  2. Connection object - poll and send process to pass value from one device to another (could cross protocols).
  3. SNVT binding - binding from a SNVT created on the Xenta Server.

Resolution

Use the following table to identify which signals types are supported and how they can be used.

Data type  Polling Connection Object  Binding
 Public Signals  Yes1  Yes1  No
 SNVT  Yes  Yes  Yes2
 SCPT/UCPT  No  No  No
 UNVT  No  No  No

1Xenta Server must be commissioned to have the TAC group address in its address table.

  • Create group bindings in TAC System Plug-in for LNS networks
  • Commission LonWorks network for Xenta Servers in Classic networks
  • Commission and download Xenta Server acting as LonWorks unit in a LonWorks group in Classic network.

2SNVTs must be created by Xbuilder on the Xenta Server device. These SVNTs are then bound using a network management tool such as LonMaker or NL-220.

Labels (3)
Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 5768
  • PeterLarsen23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore