LonMaker resynchronization fails with: Attempt to assign a neuron ID that is already in use by another device. (Subsystem: LNS, #102)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • LonMaker resynchronization fails with: Attempt to assign a neuron ID that is already in use by another device. (Subsystem: LN...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2760 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

LonMaker resynchronization fails with: Attempt to assign a neuron ID that is already in use by another device. (Subsystem: LNS, #102)

Picard Product_Support
‎2018-09-07 03:34 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:38 AM

Issue

When doing a LonMaker resynchronization, the operation fails on a certain subsystem or when doing a commission on a controller in Lonmaker an error is displayed: Attempt to assign a neuron ID that is already in use by another device. (Subsystem: LNS, #102)

Environment

LonMaker 3.X

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Cause

If re-commissioning or downloading and commissioning a controller in LonMaker fails or times out, this issue may crop up. LonMaker assigns the desired neuron ID to a temporary device while performing either of these commands, and if the operation fails, that temporary device will get stuck in the database with the same neuron ID as the controller the user was working on.

A successful resynchronization will bring this "phantom device" to light where it can be deleted, but if it is the resynch that is failing, the steps below detail how to remove a neuron ID from a device in the LNS database so it can be deleted.

Resolution

  1. Try to do a resynch command in LonMaker to get the temporary device to show itself on the Visio drawing. If this works, then the temporary device will show up with a randomly generated alpha numeric name on the same page as the controller you were trying the commission or download.
  2. After the resynch completes, delete the device from the page and repeat the commission or download. If the resynch operation fails with: Attempt to assign a neuron ID that is already in use by another device. (Subsystem: LNS, #102), continue.
  3. Because the temporary device is in the LNS database, but not on the LonMaker Visio drawing, manual manipulation of the LNS database is required to remove this object. This is done with the LNS Object Browser.

    First, shut down LonMaker, then click START and chose RUN in Windows and type lnsobjectbrowser and click ok.

  4. The Startup Preferences are shown. Set the Client/Server Communication to Don’t change and the Local Network Access to Engineering Mode and then click Ok.

  5. After choosing settings in the Startup Preferences menu, the LNS Object Browser is displayed. Press F8 to take the object browser out of read only mode.

  6. Browse to the following: ObjectServer/Networks/Your_Network_Name/Systems/ Your_Network_Name/Subsystems/All/AppDevices. Note: Double-click to open each object.

  7. Within the APPDevices menu you will see the temporary device with the large alpha-numeric name. Double-click this device to get its properties in the right hand window.

  8. Double-click on the NeuronId line in the properties pane of this device and manually set the Neuron Id to 000000000000 (12 zeros) and click Ok.

  9. Exit out of the LNS Object Browser and re-open the LonMaker database. Perform another resynchronization of the database, and the suspect temporary device should now show up on the LonMaker drawing. Then, delete that device and re-attempt your work on the original controller.
Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4021
  • tree
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore