Logs are not archiving in the ENC-520 and the error "Cannot append out-of-order or duplicate record" is being displayed
  • Logs are not archiving in the ENC-520 and the error "Cannot append out-of-order or duplicate record" is being displayed
  • sesa116873_brid
    sesa116873_brid
‎2018-09-06 09:59 AM
Logs are not archiving in the ENC-520 and the error “Cannot append out-of-order or duplicate record” is being displayed
Niagara G3, ENC-520
The timestamp of the archived logs were found to have a date code of the year 2106.  The error is because the ENC’s histories Last Timestamp is later that the ENC’s current station time.  Because of the incorrect timestamp, the ENC thinks its duplicating records so it will not append the records.  The ENC will not append any additional records to the histories until the ENC’s station time is later than the histories Last Timestamp time.
Delete the history folder from the ENC station
Make sure ENC current time is correct
  • TAC IA Series