Logging change of state events without creating trend logs.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Logging change of state events without creating trend logs.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa194431
    sesa194431

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1816 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Logging change of state events without creating trend logs.

Picard Product_Support
‎2018-09-10 12:44 AM

Issue

How to enable Vista to log change of state events without trending every point.

Environment

TAC Vista

Cause

Need to log events to monitor change of state without using trend log. 

Resolution

There are two options to enable TAC Vista to log change of state events as shown below:

Option1:

  1. Right click on the object you wish to monitor and open the properties of it.
  2. Change the watch settings from No watch to Watch.
  3. Note: Must use "Change of state" object.  It is not possible to do this under the Workstation or within a controller. 
  4. Right click on the TAC Vista and create a new folder - name the folder accordingly.
  5. Right click on the Folder which was newly created and create a new Object called change of state.
  6. Give a desired name and open the properties of the object.
  7. In General tab change the priority from 9 to Info.
  8. Select the Alarm tab set the low limit as 0 high limit as 1 and minimum change as 0.
  9. Select the object tab and navigate to the object to monitor.
  10. Close the popup by selecting OK.
  11. When ever there is change in state “on” to “off” or vice versa the event is recorded as object change in the Event view
  12. To see the events right click on the change of state object and select view events.
  13. Filter it by unselecting the alarms button on the window.
  14. Observe that events of the object are shown.

Option 2:

This needs to be done in your Menta file and it requires downloading to the controller.

  1. Open the Menta file of the desired device using edit option.
  2. Add a Alarm block to the Menta file.
  3. Connect the output / input block to the input of the Alarm block as shown.
  4. Right click on the Alarm block and select the edit option.
  5. In edit window of the Alarm block make sure the priority is set “0” (N.B. do not change it).
  6. Click on the edit button in the edit window of Alarm block and enter the desired text in the Alarm text.
  7. Steps 2 to 6 need to be repeated, if you need to do for more then one Input/Output
  8. Save the Menta file and download the same to the controller.
  9. These events are shown in Events views and not in the Alarms
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5872
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore