Log Processing Trend Log records not transferred to Extended Trend Log
  • Log Processing Trend Log records not transferred to Extended Trend Log
  • PeterEdvik
    PeterEdvik
  • Mahmoud_Sayed
    Mahmoud_Sayed
Kirk Mahmoud_Sayed Kirk
‎2021-09-23 10:28 PM
on ‎2021-09-23 10:28 PM
A Log Processing Trend Log created in an EBO server and connected to an Extended Trend Log will not transfer any records even if the Force Transfer command is executed.
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled
Log processing trend log records are not saved to database, so they will not be transferred to Extended Trend logs.
In the Basic Properties of the Log Processing Trend Log, set "Persist data" to True to store trend data in the database. This will enable the records to be transferred to the connected Extended trend Log.
  • MahmoudSayed21
100% helpful (1/1)